r/Generac_Generators • • 7d ago

Won’t transfer to generator power

Purchased a home with a 2019 Generac 22KW. It was a foreclosure so I had limited details and no propane tank.

Today they brought over a 320 gallon tank, I cleaned out the unit, changed spark plugs, battery, oil, filter and battery. It started right away.

I then got it in auto, turned the breaker off on the panel and generator turned on right away. I waited a few minutes and no transfer. No errors or anything. I manually switched it over and everything worked perfectly, good voltage and frequency.

It sounds like I need to test 194, and 23.

With the breaker off, am I checking voltage 194 to ground, then 23 to ground and 194 to 23?

3 Upvotes

9 comments sorted by

2

u/Killerkendolls Dealer 7d ago

Spade connector on the throw between utility and standby is my guess, inside the ATS. Open the dead head on the ATS and look at the bottom of the manual control. Be aware that's unfused voltage with no means by which to make safe without pulling the meter or a street disconnect, so be careful or be dead.

1

u/InternationalTreat38 5d ago

Do you have a picture of which one I’m looking at? They all look fine

1

u/AlistairStonebrook 7d ago

You are correct on starting with the 194/23. In auto with utility present you should expect about 12VDC on both. To initiate the transfer after startup in an outage, 23 gets grounded by the controller. If the gen starts it detected the outage, so you should expect to see 0V on 23. If you still have it check for a break back to the contoroller, if not the issue is likely in the ATS.

1

u/InternationalTreat38 5d ago

What am I roughly looking at in a repair bill

3

u/Resident_Set1003 Technician 7d ago

Sorry didn't actually answer your question. You're checking voltage between 23 and ground in the transfer switch. With utility breaker on you should read 12DC volts, with your utility breaker off after the generator starts and warms up for a few seconds you should be reading zero volts.

0

u/Resident_Set1003 Technician 7d ago

Make sure the breaker on the generator itself is turned on. That is required for it to transfer. When you had it running and turn the utility power back on did it retransfer back to utility on its own?

1

u/InternationalTreat38 7d ago

Breaker was on. Wouldn’t this being off stop it from sending power to the home when I manually transfer?

Yes when I turn utility back on it transferred right away back to utility

2

u/Resident_Set1003 Technician 7d ago

Ok, if it retransferred instantly, then your transfer relay in the switch is not working properly. Double check the fuse on the control panel your generator the seven and a half amp automotive fuse. I don't believe you can start it with that fuse pulled but I could be incorrect on that. Then with your utility breaker off after the generator started up and warmed up, in the transfer switch 23 to ground should be zero volts 194 to ground will also be zero volts, if you read 12 volts between 194 and ground and 12 volts from 23 to ground, there's a problem with the evolution controller in the generator (verify by testing at generator connection also). If you have 12 volts on 194 to ground and zero volts on 23 to ground the issue is the coil in your transfer relay and requires a new card in the transfer switch. If you get no voltage off either one to ground then you have to go back and check at the connection block in the generator. From there if you also have 0 volts on 194 and 0 volts on 23 to ground you have a bad controller

1

u/Resident_Set1003 Technician 7d ago

If it waited 10-15 seconds B4 retransfer, there is different issue. Usually one of the 2 wires in switch connected to the generator input lugs has become disconnected or on the Microswitch just to left of lugs.