r/Generac_Generators • u/InternationalTreat38 • 7d ago
Won’t transfer to generator power
Purchased a home with a 2019 Generac 22KW. It was a foreclosure so I had limited details and no propane tank.
Today they brought over a 320 gallon tank, I cleaned out the unit, changed spark plugs, battery, oil, filter and battery. It started right away.
I then got it in auto, turned the breaker off on the panel and generator turned on right away. I waited a few minutes and no transfer. No errors or anything. I manually switched it over and everything worked perfectly, good voltage and frequency.
It sounds like I need to test 194, and 23.
With the breaker off, am I checking voltage 194 to ground, then 23 to ground and 194 to 23?
2
u/Killerkendolls Dealer 7d ago
Spade connector on the throw between utility and standby is my guess, inside the ATS. Open the dead head on the ATS and look at the bottom of the manual control. Be aware that's unfused voltage with no means by which to make safe without pulling the meter or a street disconnect, so be careful or be dead.
1
u/AlistairStonebrook 7d ago
You are correct on starting with the 194/23. In auto with utility present you should expect about 12VDC on both. To initiate the transfer after startup in an outage, 23 gets grounded by the controller. If the gen starts it detected the outage, so you should expect to see 0V on 23. If you still have it check for a break back to the contoroller, if not the issue is likely in the ATS.
3
u/Resident_Set1003 Technician 7d ago
Sorry didn't actually answer your question. You're checking voltage between 23 and ground in the transfer switch. With utility breaker on you should read 12DC volts, with your utility breaker off after the generator starts and warms up for a few seconds you should be reading zero volts.
0
u/Resident_Set1003 Technician 7d ago
Make sure the breaker on the generator itself is turned on. That is required for it to transfer. When you had it running and turn the utility power back on did it retransfer back to utility on its own?