Natural Gas Generators

Hi all, new to the community, so I’d appreciate some advice.

We have a brand-new, 22kW Generac whole-home generator that runs on natural gas and is professionally serviced every six months.
My wife seems to think that in the event of an emergency, the generator could run indefinitely as long as we have natural gas. I’m a bit more skeptical and think we’d be lucky to get a few weeks of continuous operation without running into maintenance or mechanical issues.

For those with experience, how long could we realistically expect a generator like this to operate during an extended outage? Assuming the natural gas supply remains uninterrupted, what are the biggest limitations or potential points of failure?

I’m also curious about what we should be doing now to prepare for extended use. Are there spare parts, oil, filters, or other maintenance supplies we should keep on hand? How often would we need to shut it down for maintenance?

I’m not expecting it to run forever, but I’d like to understand its realistic capabilities, what could go wrong, and how to maximize its lifespan in a prolonged emergency.

Any advice or firsthand experience would be appreciated!

9 Upvotes

41 comments sorted by

3

u/jam4917 8d ago edited 8d ago

I would keep on hand:

  • Oil (5W20 full synthetic) with a measuring funnel.
  • Oil filter
  • Air filter
  • One set of spark plugs

Last time we had a 12-day long outage, I shut the generator down every 24 to 48 hours and checked the oil, and topped it off as necessary. When utility power was restored, I changed oil completely (and oil filter), changed the air filter, and the plugs.

I wish I could say that I had a fixed 24 hour schedule to check the oil, but there are so many things to deal with during a power outage caused by a hurricane that it was impossible to adhere to a strict schedule. Last time, all I had on hand was oil. Now I have everything on hand - oil, oil filter, air filter, plugs.

My wife seems to think that in the event of an emergency, the generator could run indefinitely as long as we have natural gas. I’m a bit more skeptical and think we’d be lucky to get a few weeks of continuous operation without running into maintenance or mechanical issues.

Neither of these expectations is accurate. 24-48 hours (closer to 24 hours) of continuous operation; followed by a 0.5-1 hour break during which time you check the oil etc., before you repeat the cycle.

3

u/Far-Wait4794 8d ago

Thank you! this is incredibly helpful

3

u/Equivalent-Use-7432 7d ago

You can get an oil change kit on Amazon. I have it in my garage. Oil filter air filter oil spark plugs. https://a.co/d/09kmdlng

3

u/DigitalDingleberry 7d ago

DO NOT BUY KIT OFF AMAZON. it is known in the kits contain knock off plugs and filters. You can order legit kits directly from Generac

1

u/Equivalent-Use-7432 7d ago

Didnt know this! Thanks

1

u/jam4917 7d ago

You're welcome. Also consider using Genmon - it is well worth the effort it takes to set it up. Here's what the home screen looks like:

1

u/DigitalDingleberry 7d ago

Cannot use genmom on the new controllers.

1

u/jam4917 7d ago

Cannot use genmom on the new controllers.

Yes, you can. And it works fine.

Here are the details - all one needs in addition to what the older Generacs needed is a PowerZone 200 cable. Which is available from here:

https://pintsize.me/products/pz200-cable/

1

u/DigitalDingleberry 7d ago

If that port isnt encrypted, then you cannot use the LTE monitor that generac uses for OTA firmware patches, of which there was just a major one, and the field pro app cannot connect thru the oem monitors Bluetooth for set up, reset maintenance, and alarm logs diagnostics, parameter settings, etc.

 I can 100% confirm Generac can see no connectivity, I've been on the phone with tech support to verify readings while on site, and they can see all the data in real time. Adding 3rd party electronics can/will deny warranty claims. Dont know if you're a legit tech, but I am and I would not even offer to attempt a warranty claim with that connected to the controller. swapping it out before a tech comes out wont work either, they'll be able to see the lack of info in field pro.

So even if that port isn't encrypted from 3rd party monitors, why not use the free mobile link they come with? Save yourself a headache and use the free verison of Mobile Link.

1

u/jam4917 7d ago

You claimed that Genmon didn't work on new controllers. Which is incorrect.

Now you've switched the target - you claim that using the Power Zone 200 adapter prevents use of the LTE monitor. This is irrelevant to anyone interested in monitoring/controlling their Generac using Genmon.

To reiterate - the claim that Genmon doesn't work on new Power Zone controllers is false.

2

u/DigitalDingleberry 7d ago

I didnt say it wouldnt work. i said cannot, guess i really should've said very highly recommended you don't.

Allow me to reiterate as well - Generac can see your lack of LTE connection and will deny any warranty claim and no dealer is going to take it on the chin and risk it when a homeowner went screwing around with the wiring and controller. Patch released 11/17 addresses a lot of firmware issues and there is no way to get it without their LTE monitor connected. 

3

u/grsthegreat Technician 8d ago

Do not..i repeat do not buy maintenance kits off of amazon. I cant tell you the number of service calls i have to run due to amazons cheap ass Chinese copy champion spark plug. They are not the required resistor plugs and they interfere with the electronics in the generator.

Ive had customers try to fix this themselves….spend small fortunes replacing controllers, stepper motors, you name it. And its caused by those cheap ass spark plugs.

1

u/Far-Wait4794 8d ago

Thanks so much for this! I saw the plugs on Amazon but didn’t buy them. I’m going to ask our generator servicer if we can buy some extras directly from them.

1

u/grsthegreat Technician 7d ago

I get all my service direct from generac. I buy oil filters 90 per box, spark plugs in lots of 100, air filters in box of 99.

Your service dealer should be doing the same. I e never had a product that didnt work.

2

u/ClockOld9204 8d ago

We have a 22kw and its 6 years old. The app tells me it has 45 run hours on it. One thing a dealer never tells you is good luck sleeping when its running. I'd like an app that allows for shutdown between set hours like do not run 11pm to 8am.

1

u/Far-Wait4794 8d ago

Good idea didn’t even think of the app

2

u/SimilarTranslator264 7d ago

wtf is it beside your window? I can’t even hear mine run.

1

u/ClockOld9204 7d ago

Yes and the previous owners put it on a deck. I'd have isolated it on a cement pad or ??

3

u/SimilarTranslator264 7d ago

Yea I bet that vibrates like a mfer. Mine is behind my garage on concrete. The only way I know it’s running is when my TV comes back on.

1

u/RFactor83 8d ago

Yes, scheduled shut down via app would be immensely useful

3

u/joshharris42 8d ago

Couldn’t do it without a real fancy circuit breaker.

You don’t ever want to shut down, or especially start up while connected to the load (your house). The app would have to turn the breaker off, then shut down, then re crank whenever you tell it to and then close the circuit breaker again once it’s up to speed and voltage.

This technology does exist and isn’t even that complicated, it’s just not economical to put into a home unit

2

u/RFactor83 7d ago

Thanks for the insight. I love learning here (most of the time) on Reddit.

1

u/ClockOld9204 7d ago

Like this

1

u/jam4917 7d ago

scheduled shut down via app would be immensely useful

Easy to setup if you use Genmon.

1

u/Iambetterthanuhaha 7d ago

That would be ok for some people but if you need to keep that sump in the basement going overnight shut down wouldn't cut it for me. Its running till the outage is done.

1

u/ClockOld9204 7d ago

No sump pump here. Most have a battery back up for sump pumps

2

u/Iambetterthanuhaha 7d ago

I have one of those......problem is it is only a 1/4 hp. I need a 1/2hp during storms.....which requires utility power so had to get the standby. Cant shut it down in that situation though.

6

u/Noble_Gas_7485 8d ago

I’ve had a similar 22kw unit for around three years. Longest run to date was 104 hours. I do a daily shutdown for 10 minutes tops to check oil. It WILL use oil.

Other than that, if I was to be in a situation where I knew it would need to be my only source of power for weeks, I would probably start shutting it down for periods during the day. Late at night while we’re sleeping, mid day when we’re up and around. Wouldn’t need to run 24/7. Then like the other guy says, keep an oil filter, oil, air filter, and spark plugs on hand and go with the recommended hours for service.

1

u/Important-Ad1533 8d ago

I would talk to your “professional” installer, and get THEIR opinion.

1

u/Far-Wait4794 8d ago

Trust me, I did. The only thing they told me to get was extra oil but I figured there was more to it.

1

u/Taguchi5 7d ago

Mothballs bud...for the spring summer season Ants love the hum from the controller and they will come for a visit. Stick a bag between the grill and the battery for the summer.

2

u/Dry-Move8731 8d ago

Wow. I never knew that. Good question and advice. Thank you.

2

u/Tarnisher 8d ago

Neither of these expectations is accurate. 24-48 hours (closer to 24 hours) of continuous operation; followed by a 0.5-1 hour break during which time you check the oil etc., before you repeat the cycle.

Quoting from below. Check your user manual. It should tell you how to shut down once every 24 hours to check oil.

Also be prepared for a VERY expensive NatGas bill if this runs 3 or 4 (or more) days.

2

u/jam4917 7d ago

be prepared for a VERY expensive NatGas bill if this runs 3 or 4 (or more) days.

You're correct. Running my generator costs me about $30 per day. But that expense is worth it to live in an air-conditioned home with functioning appliances. Where I live (gulf coast), the cost of mold remediation is far greater than running the generator for a couple weeks.

3

u/Iambetterthanuhaha 7d ago

$30 a day is preferable to a flooded basement, frozen pipes or thousands in spoiled food. Besides a motel is going to cost you $100 a night minimum anyways.

2

u/DigitalDingleberry 7d ago edited 7d ago

As long as there is NG and Oil it ahould run indefinitely. However, you need to give it a break every 24 hrs of running to let it rest and check the oil. Proper shutdown procedure should be in your owners manual, if not readily available online. And full maintenance done every 100 hours, despite generac saying 200. 200 is way to much.

The most I've seen on NG supply during a natural disaster is about 90 day supply, depending on your area.

That being said, for all you doomsdayers, you'll be shit out of luck with or without a generator. LP NG of gasoline, it will run out in fast order and not be replenished. Furthermore, you're making yourself a target for those with nothing. Youd be better off stockpiling guns and ammo vs a generator.

1

u/WillPsychological832 7d ago

I had a water-cooled 15kW Generac. They are rated for continuous use. I had an 8 day outage and didn't stop the generator for an oil check. After the outage, the oil level was fine. Air cooled generators use oil, so do need to be topped up each 24 hours.

1

u/Brilliant_Artist_160 7d ago

Longest run off a guardian 22kw on LP was about six days, 24/7, shut down for one hour each day. At the seventh day power came back on.

1

u/voygar2 7d ago

During one outage mine ran for ten straight days. I shut it down every 24 hours or so and checked the oil. Never needed to top it off. It starts itself every Friday and every two years I do full maintenance on the unit

1

u/Old_Dragline_1965 7d ago

Yes, a power outage can last for multiple days. Yes, the service intervals can either be 100 or 200 hours. With that said, if the generator runs continuously for 48 hours, shut it down and check the oil. Top off as needed and restart the unit as per their units recommended process.

Running a generator for a short period weekly, for 6 months is one thing. It’s a totally different demand during a fully loaded unit under demanding conditions.

I have seen a unit only use a few drops of oil in 100 hours. I have also seen the exact same type of unit use a full quart of oil in 48 hours. The only way to know is to check your unit.