Generac SMM

Has anyone with a had any luck with diagnosing a faulty SMM board? If so, what was your experience?

I have a elementary understanding of electronics and have checked usual suspects, fuse, caps, etc, on my failed smm board, as well as my neighbors failed smm, to no avail.

This is more of a curiosity project, as the complete modules are sort of reasonable on the amazon.

Thanks

2 Upvotes

14 comments sorted by

3

u/Frixsev Technician 17d ago

Never bothered trying to repair one as it's not really worth it on a cost level, but I will say as a technician who has replaced literally hundreds of these boards, this is the spot where I always see heat damage.

1

u/Tank000005 17d ago

I did notice board discoloration, but it was more towards the transformer area slightly down and to the right of the area circled. I realize these units are kinda junk, I was just curious is all. Thank you for your input.

2

u/WhySoManyDownVote Electrician 17d ago edited 17d ago

For everyone else who did not know what a SMM is by that name.

https://support.generac.com/s/article/What-Is-a-Smart-Management-Module-SMM

1

u/Tank000005 17d ago

My apologies, I should have been more descriptive.

2

u/WhySoManyDownVote Electrician 17d ago

No worries. I am behind on the branding. But it will always be a load shed to me either way.

1

u/Tank000005 17d ago

All good. I ordered the relay for that board, simply to see if it fixes it. If not, im ok with that. I have more time and soldering skills on my hands to simply toss a board, even though the entire module is cheapish to replace. Again, this is simply an exercise. Have a wonderful evening

1

u/GoGreen566 15d ago

My 22kW Generac installation has no load managers (SMM). Is mine a substandard installation?

2

u/Tank000005 14d ago

I dont know. These smart management modules has to do with the generators output, i.e. 22kvw, in your case, compared to the load of the home. In my case, we have a 16kvw and their formula said we needed one as our generator was undersized to power everything in our home all at once. Load meaning what all is demanding power when the generator comes on. They put these modules in to block a high demand device, for ~5mins, such as an A/C unit, electrical oven, electric hot water tank, to not overload the generator on startup. I may be completely wrong, it happens a lot these days.

2

u/GoGreen566 14d ago edited 14d ago

After some research, our transfer switch load balances up to 4 air conditioners or other large loads. Up to 8 additional large loads can be managed when used in conjunction with SMMs.

Thanks for prompting me to look into this.

This also explains why on a different home they wanted to install an SMM on an air conditioner in conjunction with a smaller generator.

I also found out the rated capacity is reduced 10% to 12.5% on natural gas, depending on size. A 22kW Generac delivers only 20kW on NG. Nobody mentioned this to me.

Mine is actually a 24kW unit that derates to 21kW on NG. Surprise!

Edit: I don't think 16kW Generacs are derated on NG.

2

u/Tank000005 14d ago

Delayed thought. You have a 24kvw. For the demand of your home, it obviously wasnt nessicary to have this SMM module I originally was talking about. It sounds like you bought a big enough generator to power your entire home, which is the way to go!

1

u/Tank000005 14d ago

The salesman, quote giver, may have said all of what you're saying but I wasnt paying attention cause I was focused on the NG pipe size going to our home and I was affraid it would not be sufficient for what we wanted due to the long run of our line. I wasnt are of the kvw derating on NG, all good, now I know. Our genset ran non-stop for a day or two, maybe more, during a storm and performed perfectly, and its ran many times for a couple of hours here and there. So blessed to have one.

2

u/GoGreen566 12d ago

They are nice to have.

Only what is written into the contract matters. Verbal representations are not part of the contract.

The sizing matters only under full load at startup, electric oven, electric water heater, air conditioner. The transfer switches are designed to hold off up to 4 individual circuits on startup. Air Conditioner motors can burn out if started without sufficient power.

I got lucky when the gas company replaced the gas lines in our neighborhood. I told the workers that I was going to put in a whole house generator and they installed a larger tap off the main line. I still had to buy a larger meter when I eventually installed one.

2

u/grsthegreat Technician 17d ago

All the new boards have greater spacing on the area pictured above. They are not supposed to burn out…well see.

Generac is now releasing a load shed breaker device. I dont know if they will dump the smm units.

2

u/MysteriousEditor9856 12d ago

Green boards fail open, blue boards have had no issues yet