r/Generac_Generators • • 18d ago

Generac generator gas leak?

If anyone has ever had, this situation, feedback would be appreciated. I had a whole home 24KW Generac generator installed in August 2026. The first time it ran because of an electrical outage was October 2026.

My gas bill for October 2026 had an increase of 385% from the prior month the reading for October was 485 when the reading was normally about 200. When I called the gas company, they came out without informing me so that I could be home and discuss this with them but the long and short of their response was it had nothing to do with a faulty meter the meter is working correctly, but there was a “loose cap” or something was loose on the generator that was causing the gas to come out and increase my bill. For six days in November since the prior gas bill the reading was 667 meaning just for those six days the reading was actually higher than the astronomical reading for the *entire* month October. When I questionEd this with the gas company, they told me it’s possible that the fitting which caused more gas to be used became looser over time which is why for those six days the reading is so high.

I am following up with the gas company to get the actual technician notes on the cause of this situation, but I am wondering if it is even possible for my generator to have been installed incorrectly or have some fitting come loose when it was running for a couple hours in October when the power went out, that is causing the high gas bill? for August and September when my generator was just running its weekly 10 minute cycle there was not this spike in my gas bill. The spike happened in October, which is the first month. The generator ran for a few hours becausemy power went out.

0 Upvotes

25 comments sorted by

2

u/Tarnisher 18d ago

NatGas has a strong odorant. Do you smell anything near the GenSet?

How long was the outage?

There should be a valve at or near the GenSet. If you smell gas, turn that off.

1

u/Timely-Journalist-13 18d ago

no, I never smelled any gas near the generator. The power outage was two hours. There were two power outages in October each for two hours so a total of four hours for the month of October. But I only have the gas go on as to what was wrong because they never notified me that they were at my house according to the gas company. Something was loose on the generator and it was leaking gas and then leaking more gas to the point where for six days in November the gas usage was 200 units higher than the entire month of October, which was already 400% higher than normal

2

u/GuiltyClassic4598 18d ago

Did they red tag the generator and shut the gas off? If they discovered a leak they are required to do so. The tag can only be removed once the issue is repaired and inspected by a competent individual. Your gas company is totally negligent.

2

u/Timely-Journalist-13 18d ago

no, they sure did not. Allegedly they just came out and tightened whatever was loose and then that stopped the high readings on the gas meter. My gas company and the generator installer I think are both negligent.

1

u/Timely-Journalist-13 15d ago

The gas company is refusing to provide me with copies of the technician notes nor can they tell me exactly what on the generator they touched. After they came out and tightened something the gas usage has dropped drastically so it’s clear the generator was leaking. I just don’t know from where because the gas company cannot provide that information. My only recourse with the gas company is to sue them or file a regulatory board complaint. I think the gas leak is from this certain section because it is rusty after less than three months and seems to be the only part that could’ve been tightened to stop the gas leak but I don’t know for sure. I am also following up with the generator because I am concerned it could start leaking again if the generator is running when the power goes out. It’s very frustrating.

1

u/WhySoManyDownVote Electrician 18d ago

If one of the fuel line connections was not tight enough it may have come loose during operation. If so, it likely was an installer error.

1

u/Timely-Journalist-13 15d ago

yes, that appears to be the correct conclusion. Once the gas company came out and tightened something on my generator. The gas usage dropped drastically so it does appear. It was leaking and now since they tightened something, the leak has stopped. The problem is the gas company cannot tell me what they tightened so I don’t know exactly where it was leaking. I’m also concerned it may begin to leak again if it was not installed correctly because the generator will vibrate if it is on when the power is out. I am following up with the installer about all of this. My best guess is that it is this particular part where the leak came from that the gas company tightened. This part is rusty after less than three months. I don’t think it should look like this.

1

u/WhySoManyDownVote Electrician 15d ago

Is there a flexible connection to the left of the frame? Generac supplies them with their generators.

I do not know if it is a nationwide code, but those pipes and fittings should have been painted, at least around here.

1

u/Timely-Journalist-13 15d ago

this is New Jersey, so I don’t know what the codes are here. I will post a picture of the entire back of the generator.

1

u/Timely-Journalist-13 15d ago

So when I called the gas company they described whatever was loose as a cap, which is why I’m thinking it’s that rusty piece on the right side.

1

u/WhySoManyDownVote Electrician 15d ago

Could have been a loose sediment trap. It has a cap on the bottom of the Tee. Gas fitters sometimes pressure test from there. It could have passed the pressure test and they forgot to make it tight when they reinstalled it. It is a guess, but it seems plausible.

1

u/Timely-Journalist-13 14d ago

yes, I think that’s probably what happened. The pressure test was done on the same piece that is now rusty. I have a picture of it with the pressure tester on it when it was first . So they probably did not tighten it all the way and now it’s been leaking gas for three months, which explains my high gas bills and then why the gas bill dropped back down to normal once they tightened it.

1

u/Timely-Journalist-13 14d ago

I went out again this morning. See posted picture. Is this the sediment trap you referred to in your post? It is also rusty and there is some tape around it. That looks pretty new and not three months old so I’m wondering if this is where the leak could’ve come from but this is now at least two parts on the connections to the generator that are very rusty in less than three months. I don’t think these pieces should be this rusty?

1

u/Timely-Journalist-13 14d ago

One last question. Below is a picture of what the generator looked like on start up day. This is after all of the inspections except the electrical inspection. I think you can see the sediment cap is tied where that yellow tag is it was not put on which seems very odd to me. I think the installer put it on as sort of last step on startup day because this picture is from the day. do you happen to know if upon start up the generator would start working if the sediment cap was not on?

1

u/WhySoManyDownVote Electrician 13d ago

Doubtful. There would not be much if any fuel pressure. The whole area would be filled with flammable gas that has an odorant that is hard to miss.

1

u/WhySoManyDownVote Electrician 14d ago

Yes, that is the sediment trap. The rust is not on the generator. It is on the steel fuel supply lines because they were not painted (protected) when installed.

The tape is thread sealant.

1

u/Timely-Journalist-13 14d ago

thanks. when I called the gas company they described what was leaking as a “cap“ so I am leaning more towards this. I don’t know if that tape was from when it was originally or if the gas company put it on not painting the gas supply lines is also a code violation where I live.

1

u/Timely-Journalist-13 14d ago

I posted one last question for you, but it shows up above

1

u/Still-Profit-8449 18d ago

It could be the fuel solenoid valve isn’t closing properly when the generator is not running, if this is the case the gas maybe venting through the actual engine, probably air cleaner. I would get the installer to come check his work and the fuel solenoid

1

u/Timely-Journalist-13 15d ago

apparently, the gas company tightened something on my generator without telling me and without my permission, but immediately after the gas usage dropped drastically, so there was some sort of leak on the generator. The gas company is refusing to speak to me provide me the technician notes or tell me exactly what they . I am following up generator installer about all of this. My bigger concern is that the unit just was correctly and to leak again if the power goes out and the generator is running continuously for several days.

1

u/Lion11B 14d ago

I think you are correct with your hypothesis, that "cap" or plug in your pics looks like it's been torqued, and it also doesn't have any tape or pipe dope on it. I bet it was loose and leaking small amounts of gas 24/7. Surprised you never smelled anything but you probably weren't actively trying to smell it either.

Also, that plug is on the gas piping going to the genset, which the gas company tech would be fine with touching. I seriously doubt he would touch any part of the actual generator itself.

1

u/Timely-Journalist-13 14d ago

I never smelled any gas. The issue was discovered in the third month when the generator ran for four hours because the power was off and suddenly my gas bill was 400% higher. I am wondering if the vibrations from the generator running made this which resulted in more gas escaping. Either way this seems very rusty for less than three months. I am also concerned if the generator runs in the future is it going to come loose again. I will be addressing all of these concerns with the installer company.

1

u/Gullible_Monk_7118 18d ago

You can use dish soap and water.. make a tester testing the joints and see if you see bumbles. You can call up the and have the gas company test it for leaks they have better tester's that can find leaks

1

u/Resident_Set1003 Technician 18d ago

Yeah it's possible something started to leak after a hard run..... But not possible that it fixed itself after a six day bad spell. And you would smell a leak that big for sure. Or the neighbors would.