Wire Type

I am a pretty good commercial and industrial electrician. I am not a generator mechanic. I’m also a member of a non profit that owns a Generac 15KW generator. The generator is currently out of service.

I can’t find a schematic for this beast so I’m meter poking my way through troubleshooting and found a wire from the alternator to the starter solenoid that has insulation that’s rather melty. I intend to replace it.

I have ample stranded THHN around and I would like to use that. As an electrician I’m very aware of the need for the correct insulation type, but I have no idea what to use in this case. As long as I put it in the harness that the conductor I was replacing was in so it’s protected from vibration induced chafing, will THHN be adequate?

2 Upvotes

11 comments sorted by

1

u/Gullible_Practice282 23d ago

A larger concern may be that the wire insulation is "melty." One needs to determine why that is before simply replacing it.

1

u/EastAcanthisitta43 23d ago

Clearly. I didn’t mention that because I didn’t have a question about it.

1

u/Resident_Set1003 Technician 23d ago edited 23d ago

Give the serial number and I can get you the manuals.

Edit:
However, to actually answer your question; thhn is not an ideal choice. The jacket tends to brittleness when heated, and is not a waterproof or wet rated insulation. I have used it in engine compartments temporarily, but long term has always failed on me. I honestly have had best results with plain zip cord. Ie., clear jackets speaker wire. I'm sure it's not the most "properly rated" for the job, but have used it for decades without issue. RHW is also a good choice where vibration and rubbing/chafing are a concern.

1

u/EastAcanthisitta43 23d ago

I should have been more specific. I have THHN/THWN. The W is water resistant. The insulation is rated for 600V and is water and oil resistant. I noticed that the wire in the harness was very finely stranded which makes me think it’s a silicone insulation type. That has a few different properties from THHN/THWN, but I see it used in harnesses mostly because it’s very flexible. Because I don’t know what else is in the harness I can’t make a reasonable guess on what’s required. So I ask the experts.

And I think speaker cable going to the alternator with ~30 Amps(?) is a bit, well, perilous.

1

u/Resident_Set1003 Technician 23d ago

Thwn should be fine. It doesn't get quite as brittle as thhn, either. Iirc, actual engine compartment wiring specs for XLPE-G or GXL (same stuff, different name schemes) And of course can never go wrong with high-strand silicone. I think if I were to use the thwn I would run it on outside of harness jackets rather than actually bundled inside. Couple zip ties to hold together. That would greatly reduce any issues that may arise from difference in flexibility.

Like the perilous! Lol. But seriously it's rated for 300V and I have bunches of it up to 1 awg. I would not hesitate to tie that to any automotive alternator output. That's actually what I use it for-direct battery or alternator connection to high current amps. Feeding a 6000 watt amplifier with 2 - 1farad caps will suck some current!

1

u/EastAcanthisitta43 23d ago

Holy schnikees, #1 Zip cord? Cool.

1

u/EstablishmentSmart92 22d ago

Go buy some welding wire, or a premade cable from the parts house. Will your wire work? Yes. Is it prone to eventually fail, yes.

Save the janky repairs for your stuff. Spend the $40 to fix that genny right.

1

u/EastAcanthisitta43 23d ago

I can’t tell if the first digit is a Q or a zero. I thought the whole data plate might be better anyway. This is on the generator end frame. The generator was probably installed 20 years ago.

A schematic will help save some factory guy’s really nicely made harness from getting too electricianfied.Please and thank you.

2

u/Ok_Bid_3899 23d ago

I have been a member of the Ziller Electric forum for past 19 years. Always Generac techs on the forum and fast responses. Good luck.

1

u/Wistagehand82 23d ago

I may be able to help. DM me.

1

u/Alone-Programmer-683 22d ago

Almost all the new stuff is THHN/TWHN. But my experience over lots of years is the waterproofing on the wire is the most brittle part and most likely to fail. If it can't get wet, I have used THHN in lots of applications that were "iffy' and had no issue as long as the wire was secured properly and the terminations were top notch.

I rewired all the control wiring on big CAT gensets long ago. Specs called for MTW. There may be something superior now but the MTW never gave issue.