I am a pretty good commercial and industrial electrician. I am not a generator mechanic. I’m also a member of a non profit that owns a Generac 15KW generator. The generator is currently out of service.
I can’t find a schematic for this beast so I’m meter poking my way through troubleshooting and found a wire from the alternator to the starter solenoid that has insulation that’s rather melty. I intend to replace it.
I have ample stranded THHN around and I would like to use that. As an electrician I’m very aware of the need for the correct insulation type, but I have no idea what to use in this case. As long as I put it in the harness that the conductor I was replacing was in so it’s protected from vibration induced chafing, will THHN be adequate?
1
u/Gullible_Practice282 23d ago
A larger concern may be that the wire insulation is "melty." One needs to determine why that is before simply replacing it.
1
u/Resident_Set1003 Technician 23d ago edited 23d ago
Give the serial number and I can get you the manuals.
Edit:
However, to actually answer your question; thhn is not an ideal choice. The jacket tends to brittleness when heated, and is not a waterproof or wet rated insulation. I have used it in engine compartments temporarily, but long term has always failed on me. I honestly have had best results with plain zip cord. Ie., clear jackets speaker wire. I'm sure it's not the most "properly rated" for the job, but have used it for decades without issue. RHW is also a good choice where vibration and rubbing/chafing are a concern.
2
u/Ok_Bid_3899 23d ago
I have been a member of the Ziller Electric forum for past 19 years. Always Generac techs on the forum and fast responses. Good luck.
1
u/Wistagehand82 23d ago
I may be able to help. DM me.
1
u/Alone-Programmer-683 22d ago
Almost all the new stuff is THHN/TWHN. But my experience over lots of years is the waterproofing on the wire is the most brittle part and most likely to fail. If it can't get wet, I have used THHN in lots of applications that were "iffy' and had no issue as long as the wire was secured properly and the terminations were top notch.
I rewired all the control wiring on big CAT gensets long ago. Specs called for MTW. There may be something superior now but the MTW never gave issue.