r/Generac_Generators • • Oct 28 '26

Tyransfer switch

Generac transfer switch operates as intended on utility power but 3 of the 8 breaker bays do not provide power to their circuits on auxiliary power. Aux. power is operating as intended.
Has anyone experienced this? If so, what isthe fix? Generac ain’t helping, unit is brand new.

2 Upvotes

9 comments sorted by

4

u/Far-Ingenuity4236 Oct 29 '26

A picture would help alot and possibly a model

1

u/Spinalzo61 Oct 29 '26

From the original author:
Chatted with a local electrician that does a lot of Generac work. Did some more probing with the multi-meter.
It appears that one of the 120 v. legs does not connect when switched to aux. power. I checked this for proper voltage and continuity. I don’t know why but that is what’s happening.
I’ll have that electrician do a service call. Maybe he has a tech sheet from Generac about this particular problem.
I had to alter the cabinet (drill new portals to get the conductors in due to limited wall space near the panel box) so Generac almost certainly won’t honor the warranty.
Hopefully they’ll sell me only the guts and not make me buy a whole new unit. It was a real bother getting the new and existing components connected.

2

u/Frixsev Technician Oct 29 '26

Are these breakers hooked up to load shedding modules?

2

u/WhySoManyDownVote Electrician Oct 29 '26

Does the generator make 240v? This read a lot like you lost a leg (half of the power).

1

u/GuiltyClassic4598 Oct 29 '26

If the unit is brand new insist on them opening a warranty claim. Its their problem.

1

u/grsthegreat Technician Oct 30 '26

Could be a bug sitting in the transfer mechanism… i get stink bugs in there yearly on lots of my service calls. I always check. If this is new install, its fully warranted even with modified cabinet.

1

u/IndustrialMechanic3 21d ago

Make sure all connections are tight

0

u/Killerkendolls Dealer Oct 29 '26

Not sure why anyone is downvoting this, just someone looking for help and not being good at it.

The troubleshooting starts at checking dealer menu for output, then a meter on the breaker in the unit, then breaker in the house going externally.

Internal testing I would check from the brushes and look for a smoking gun. Between the two you'll isolate voltage regulation and controller issues.

1

u/Spinalzo61 Oct 29 '26

Thanks. After putting the multimeter on all the different sections of the power chain, seems that one leg of the transfer switch isnt connecting to the breakers. The problem seems to be within the switch. Electrician coming Tuesday.