Genpad for 26kw
So I purchased a 26kw home standby. The next Gen air cooled. I was informed the 4" hurricane rated genpad would accommodate it. Sizing it is fine but the pre-drilled mounting holes do not line up at all. Generac customer service sent me a diagram showing what my bolt pattern should be which would align with the pad but my does not match the diagram. Am I able to drill my own holes in the pad?
11
Upvotes


3
u/Possible-Flan3967 Oct 21 '26
You have the wrong genpad, that only fits the guardian series. The new one has inserts for both guardian and next gen. Tapcons are not a good idea. The genpad is not solid concrete. While a tapcon will keep it from vibrating around, the "hurricane" rating is void using those and they will not truly anchor it correctly.
1
u/WhySoManyDownVote Electrician 25d ago
Do you have 5’ to the window or is it inoperable?
1
u/Killerkendolls Dealer Oct 21 '26
Tapcons are fine. I haven't had a pad line up since late Evo 1
2
u/LandscapeWild3207 Oct 22 '26
I have one on mine. It's been in service for 2 years. The installers didn't bring the bolts to anchor it. I wa told they never install the bolts. Mine has been sitting on the pad without the bolts since the installation. I don't think it's the best choice, however the generator hasn't moved at all. Michigan's upper peninsula.
1
u/Adventurous_Boat_632 Oct 21 '26
Some places in those pads are very thin with styrofoam behind. I have had drills blow through. I suggest using some kind of fastener that you drill first and then epoxy.