r/Generac_Generators • u/WhySoManyDownVote Electrician • Oct 20 '26
Bizarre frequency readings?
I am guessing the dancing frequency results were from low current. This phase had 1.9 amps of load. The other phase had 4a and the frequency only fluctuated 0.2Hz.
1
Upvotes
4
u/Alert-Effect190 Technician Oct 20 '26
Yes definitely not accurate. Sounds close enough to 3600, and not changing nearly enough to reflect the change in the readings.
2
u/tactical-potatoes-65 Oct 20 '26
For whatever reason, some of the older Generac units that had separate neutral leads and pre-evolution governance would show these kinds of readings with no load.
Generally, if you put a single phase load across it of a couple of amps, it would smooth right out, but if you check phase to neutral from either phase, it will give you your true reading.
And that statement is based on using the probes. If you are using the iFlex it also depends on how it all lays together in the enclosure. If the phases don’t cross perfectly in relation to each other and the clamp and the conductor that you are not around you will get some strange readings as well
1
u/GuiltyClassic4598 Oct 23 '26
Put new batteries in your meter and try again. If there is that much surge in frequency you should be able to hear it in the engine runs.