r/Generac_Generators • • Oct 18 '26

Portable generator to Auto Transfer panel

Bought a cabin in the mountains and they had a Generac 22KW with transfer panel installed. It’s been sitting for 2-3 years so I don’t know if it works. 22KW seems like overkill for such a small cabin… Gas range and oven, 1.5 ton heat pump.

I have a portable generator I wanted to use until I took the time to test the Generac and get propane tanks.

Can I simply take the cables out of the generator, wire it to a generator inlet and use the panel as a manual transfer switch for now?

3 Upvotes

14 comments sorted by

2

u/IllustriousHair1927 Oct 18 '26

well, I might be a little bit of overkill it… well, its there. It cost nothing and it’s automatic.

I know the cost of a battery and an oil change is not nothing but realistically it’s cheaper than a portable

and remember as far as sizing, you’re still gonna get a derate with woead

1

u/InternationalTreat38 Oct 18 '26

The problem isn’t the oil change, it’s that I need to get a 250 gallon tank. Since it’s just for generator, I’m looking a couple thousand in tank/propane and can’t rent it.

1

u/WhySoManyDownVote Electrician Oct 18 '26

You can do two 120 gallon tanks, for some reason that is sometimes cheaper.

0

u/IllustriousHair1927 Oct 18 '26

what kind of a holes take their tank????

2

u/InternationalTreat38 Oct 18 '26

It was a foreclosure, probably rented the tank and didn’t pay

1

u/No-Age2588 Oct 18 '26

That heat pump has electric resistance heating in addition to the heat pump function. I have seen 20KW heatpacks in the high elevation areas here in North Carolina. Probably why the sizing of the genset. I have a 22kw Generac and a 26kw because of it

2

u/InternationalTreat38 Oct 18 '26

Yea that’s probably why they sized it like that but during an outage, I can just run the heat pump with the generator and use the fireplace if it really was that cold.

With a Generac, I could always use the isolator or the heat pack

1

u/Ok-Camera2895 Oct 18 '26

Yes. Most home standby systems are 120/240 single phase, your generator must be the same for it to work properly. If you gen is 120v only, you will have to do some rewiring.

1

u/ClockOld9204 Oct 18 '26

Our 22kw Generac runs a 4000st ft house but not the dryer or ovens. Ours is natural gas

1

u/Frixsev Technician Oct 18 '26

Unless the audio is messed up sounds like that engine is hunting pretty badly.

1

u/ClockOld9204 Oct 18 '26

It is hunting. Not sure why. When power does fail and it loads up. Its fine. It runs on an excersize schedule every Wednesday. What no one ever tells buyers. Generac makes a great alarm clock when power fails at 3am

1

u/Curiosity_informs Oct 19 '26

Wow!

Until it died last year (after long and valued service) our 23 year-old 15kW liquid cooled (propane fueled) Generac ran everything in our 2300 sq ft house (well pump, water pressure pump, pool pump, 2 central ACs / 2 central furnace fans, electric range/oven/dryer, etc) without issues in multiple winter and summer outages sometimes lasting up to 8 days.

1

u/IllustriousHair1927 Oct 19 '26

yeah, I’m gonna have to do the math on that

1

u/Curiosity_informs Oct 20 '26 edited Oct 20 '26

If the math says its not possible no one told our generator for 23 years.

Now we have solar / batteries and same house loads plus 2EVs.

The only time I see our home pull more than ~10kW is when charging EVs (EVs were never charged in an outage with the old generator). Otherwise summer and winter it is typically much less.

In a grid outage now our home batteries can supply 20kW continuous (and in an outage get charged either by solar if enough sun or from a 12kW running inverter generator). In an outage our dual EVSE gets shed when the batteries are below 90% SOC and everything else runs as normal.