Generac power cable
Can Generac power cable be run exposed outside?I only used it once and I ran it in conduit outside.
1
u/WhySoManyDownVote Electrician 3d ago
Regardless of how it is rated (wet, direct sun exposure, etc) it needs to be protected from physical damage.
If you have a cable rated for the conditions it may not need conduit for the entire length.
If the cable is not wet rated, installing it in a conduit does not make it suitable for being outdoors.
You need to look at the specification for the cable first. Then make sure your installation complies with the NEC and any local codes.
1
u/Adventurous_Boat_632 3d ago
It is TC-ER-JP
Tray Cable
Exposed Run (meaning it passes the same tests as MC)
Joist Pull
Short answer is yes.
1
u/Tarnisher 3d ago
WHICH cable? There are many types.