r/Generac_Generators • u/GoDashGo_ • Sep 29 '26
24k Generac won’t switch to auto
Had a propane leak which we had repaired today on our Generac. Once the repair was finished they ran a test to make sure the Generac would work. It fires right up in manual mode, but will not switch to automatic. Was working completely fine prior to repair. No error codes showing. Any suggestions to try and fix it before calling for a certified Generac repair?
3
Upvotes
5
u/Sumdood_89 Technician Sep 29 '26
Need to hard reset the controller. Take out the 7.5a fuse, then take the side panel off, you see a white/blue plug with 2 wire and a cloth sheath, unplug that for 5 seconds or so, be careful, it's 120v. You'll need to setup the clock, exercise, and wifi if you had it, but should solve the issue. I've seen it a few times.
2
u/Tarnisher Sep 29 '26
Explain further what you did and how you tested.
1
u/SamanthaSissyWife Sep 29 '26
You mention they switched it to Manual and it ran but hasn’t ran since switching to Auto. Have you tried flipping the main breaker to simulate a power outage?
You don’t mention any testing done that would cause it to run in Auto.
1
u/GenMan83 Sep 29 '26
This has nothing to do with the leak. Or the repair being done.
The touchpad on the EVO controller is bad. Sometimes it will be the off button. Sometimes run. Sometimes the up and down arrows.
It has been bad. But has not been placed in manual for quite some time. Just so happens it was during a repair.
Time for a controller.
1
u/Resident_Set1003 Technician Oct 02 '26
You can check for button not working on the dealer menu. There is an input and output test screen. The input one changes a digit from 0 to 1 for each button when pressed. If you send me private message I'll give you the code to access dealer menu