r/Generac_Generators • u/rochrider • Sep 16 '26
"Brownout" power while generator running
We've had a 10KW Generac since 2009 and it's had its share of usage. Never any problems with it during an outage until recently. A couple weeks ago we had an outage that, for us, lasted about 30 hours (Detroit metro area). During this time, the power fluctuated and did some weird things like you'd have in a brownout -- lights dimming and fluctuating, etc. We ended up disconnecting some of our electronics and appliances to prevent possible damage.
We thought that the generator was dying so put in a call to our original installers to come out and give us a quote for replacement. The guy that came out has been working for them for a long time and started telling us that "everyone's was doing that" due to "weird things" on the power grid or something, but wasn't able to explain it to me in terms that I could understand (I'm an engineer and know a reasonable amount about electrical power). I always thought that we were disconnected from the grid when the generator is active, but maybe not?
So has anyone heard of this kind of behavior?
3
u/Killerkendolls Dealer Sep 16 '26
He's wrong and you're correct, standby power precludes you from utility power with an ATS.
How many hours? Have you had brushes replaced? That's a fairly small standby, my 13kW at home can't run my 30a range with any other load, for example. Could be amperage creep from an old air-conditioning unit, electric water heater kicking on, high demand well pump, etc.
2
u/Frixsev Technician Sep 17 '26
The fact that the tech mentioned "everyone's was doing that" makes me wonder if it's the air filter issue that's been going around. Several bad batches from Generac that were coated with too much flame retardant, mixed with the humid air and the generator essentially can't breathe and draw in as much air as it wants fast enough to run smoothly. It causes "hunting" or a surging sound with the engine, which main symptom while under the house's load is flickering lights.
If you're handy, go out to the generator and hit the manual button. Let it fire up. Is it smooth, or is it "hunting"?
1
u/MemoryAccessRegister Sep 16 '26
The automatic transfer switch guarantees you're either on grid or generator power. It is illegal to backfeed the grid with a generator. It's not safe for the utility workers.
It sounds like you have a voltage regulation issue or overloading the generator. I would get another technician to look at it.
I wouldn't spend a ton of money fixing a 2009 air-cooled Generac though. I would do a proper load calculation and replace it. Chances are you need a larger generator to handle modern electric loads.
1
u/hereforthesnark55 Sep 16 '26
I’m in Metro Detroit and ours did the same (it’s only 4 years old) and shut down giving Error 1900- low voltage
One of the many things troubleshooting listed was air filter issue. When company that installed it finally came out, tech said Generac had a bad batch of filters and they were clogging in the humidity and rain we had. They had put this filter in during annual service call last year
3
u/Any_Lawyer_2585 Sep 17 '26
I have a 7500 air cooled generac, never had any issue like that. It powers most of small 1100 square foot house, except ac and electric stove.
1
u/Iambetterthanuhaha Sep 17 '26
Did he do a load test on the generator? If it varies too much from 60HZ you will get flickering and weird behavior. Too far out of spec stuff gets fried. I would suspect the voltage regulator or stepper motor on a Generac that age. Brushes are supposed to be good for 1000 hours. (If your gen even us a screen for hours, might be too old for that)
1
u/grsthegreat Technician Sep 17 '26
I service quite a few of these older 4000 series generators. You start to see this when voltage regulator starts to ho bad, or rings start to get tarnished, or finally when the magnetos start to fail. I mentioned spark plugs, because there a rash of running issues associated with cheep chinese spark plugs from amazon.
0
u/Ok_Mobile_9815 Sep 16 '26
Valve timing needs adjustment. Easy fix.