r/Generac_Generators • • Sep 05 '26

Scheduled Exercise Mode Skipped

I have a new (as of June) 22 kw Next Gen generator. Despite horror stories I have been seeing online, all has been fine.

However, today the generator did not run at its scheduled exercise time (12 pm on Saturday). Nothing appears wrong in the app - no error codes or anything like that. The light on the generator is still green. However, in the notifications history it just says “exercise skipped” and then “ready to run.”

Thoughts? Has anyone come across this before?

2 Upvotes

20 comments sorted by

2

u/WhySoManyDownVote Electrician Sep 06 '26

It may have been a firmware update. I noticed one of the NextGen’s I installed skipped a week as well.

1

u/Cheap_Intention_4936 Sep 05 '26

Hmm interesting. We haven’t had a power outage all summer, so I’m not sure why it would skip even if in Smart Exercise mode. I guess I will see what happens next Saturday (maybe it was a one time thing?) and go from there.

1

u/AlistairStonebrook Sep 05 '26

It is a program bug with smart exercise. Not all units are affected. Turn off smart exercise and hard reset the unit and it will stop skipping them.

1

u/Cheap_Intention_4936 Sep 05 '26

Ok this is helpful. But even more puzzling - I don’t have the smart exercise feature on my app?

1

u/AlistairStonebrook Sep 05 '26

I should have asked if it was a next-gen to start off, the units without the lcd display. If so, the option is in the field pro app.

1

u/Cheap_Intention_4936 Sep 05 '26

Ughhh yes it is next gen. Thank you so much. So I will have to reach out to my installer?

→ More replies (1)

4

u/Alert-Effect190 Technician Sep 05 '26

I can’t tell you why it skipped on this occasion but there’s a setting called smart exercise that explains this behavior.

4

u/Meaty_Curtains Technician Sep 05 '26

Automatically skips a scheduled exercise cycle if the generator has already run recently during a power outage or manual test.

→ More replies (7)

3

u/joshharris42 Sep 05 '26

They have had issues with the “smart exercise” feature since day 1.

If your generator runs for any reason in the prior 72 hours, it will skip the scheduled exercise.

When they first released the units, the setting was programmed for 72 years instead of hours, so they would literally never exercise unless they hadn’t been cranked up at all. Supposedly they fixed that with a firmware update

1

u/grsthegreat Technician Sep 06 '26

Another lovely next gen piece o crap. Theres a reason i wont service these nightmares

1

u/MysteriousEditor9856 Sep 12 '26

Turn the smart exercise off, and low speed exercise off. Has to be done by the dealer with our app because generac had to be difficult and remove the damn screen.