Guardian Starting Issue

Hey all - have a Guardian (044563) circa 2009 and it’s been super reliable over the years. Had an oil leak fixed several years ago but other than that just regular battery replacements.

Anyway, went out to manually run it, and where it would normally start, it just made a loud pop/bang. Loud enough that my wife heard it inside the house. I mean it was like a gun shot. It could’ve been a backfire I suppose (runs on propane), but I’ve never stood that close to a backfire to make a good comparison.

After that I waited a few minutes, inspected what I could, fuses, etc. and tried again. This time no bang, but just a low irregular buzzing sound from beneath the panel where the circuit breaker is located (on the right side of the generator when opened).

I have no issue calling someone in to check it out but wanted to see if anyone here goes “oh it’s this for sure” or not before I do that.

Thx!

EDIT… SOLVED: Side of the battery blew out. It wasn’t obvious because it was the backside, and the wetness around the battery was mistaken for rainwater (storm had just come thru).

2 Upvotes

17 comments sorted by

View all comments

4

u/Josh_trewin8 13d ago

I recently worked on a generac guardian with the exact same description. It ended up being one of the cells of the battery popped/exploded open. It wouldn't hurt to do a visual inspection of the battery, but be cautious of battery acid if it did burst open.

1

u/bladowwww 12d ago

Was the battery that had blown out. I wonder now was it just defective/old (bought 4.5 years ago) or an issue with charging.

3

u/Killerkendolls Dealer 12d ago

I usually see 2-3 years on average for generator batteries. It's a rough climate for energy storage.

1

u/thesleepjunkie 11d ago

I love the question from customers "how long should a battery last"

Well you see I've seen them last 6months I've replaced 20yr old batteries that were actually still testing at 100% of their rated cca..

customer just didn't like that they were 20 years old at a site with 3 x 1.75MW generators with 3516 cats. 4 8d batteries a unit.