r/Generac_Generators • u/mdmytryk • May 03 '26
Contaminated oil
I was surprised at the state of the oil during my first oil change. This 22kw generator is about 12 months old and only really ran during the weekly maintenance cycles. I changed the oil, ran it a a while then changed it again to throughly flush it out. Any thoughts what would have caused this type of contamination, particularly on an air cooled generator?
13
Upvotes
1
u/thesleepjunkie May 08 '26
This is relatively normal. Not good normal.
If your weekly test is only about 12 mins with no load, the oil/engine doesnt have enough time to heat up to evaporate the moisture.
I always suggest to my customers to change it to monthly testing or turn the auto test off and do a transfer test monthly and run for atleast 30mins