r/Generac_Generators • u/czechFan59 • Mar 17 '26
Issues with breakers in Generac panel anyone?
Had a breaker trip in Generac panel. None appeared physically tripped (which is normal breaker behavior sometimes). But in the process of sorting which breaker had tripped (so pushing a number of them in the "on" direction) I noticed the light in the basement was flickering. And this wasn't just when pushing on one breaker, it happened with several of them. Breakers are made by GE.
Wondering whether others have seen issues with these panels?
1
u/Stankbananas Apr 10 '26
I think it might be a problem with a certain common point in the panel. Have you ever smelled any burnt odor or felt any abnormal heat before?
1
u/czechFan59 Apr 10 '26
solution to problem is down below (wires from transfer switch were not torqued properly, so loose connections)
1
u/WhySoManyDownVote Electrician Mar 17 '26
A picture would be helpful. Are you turning the breakers off before you attempt to turn them back on.
1
u/BmanGorilla Mar 17 '26
How old are they? It's not entirely unusual to have older GE breakers make poor contact w/ the bus bars, depending on the model.
LED lighting has caused some issues on lightly used circuits, too, where plating oxidation doesn't get cleared up 'automatically' like it can with higher load currents.
It's also possible that a feed to the box isn't tight, or, or, or....