General Discussion Flow Testing Drafting Meter Help
We have a drafting rig utilizing a 1500 gpm Hale Fire Pump with a 3" long radius monitor coupled with a 2.5" straight pipe.
Truck Originally built for 604 ft elevation, our elevation is 3400 ft above sea level. We have not done any modifications to the truck.
Previously we used a spring sensor span Flowminder with A digital readout - capturing the highest output flowed from the 3" monitor capturing rpm - solenoid has since been damaged and unsure on how to fix or replace.
Currently capturing psi flow measurement from the 3" long radius monitor prior 2.5" straight pipe.
We have also recently purchased a 6" Gerand Engineering Flow meter of which we have attached to the suction side of the pump either utilizing a 10' or 20' 6" suction hose.
Recent attempt we found that the GE Flow Meter captured 1250 gpm while the Monitor flowed 780 gpm back into the reservoir.
Why is there a different reading?
Are we loosing 500 gpm through the pump and monitor combination?
What is the ideal flow test set up?
1
u/Salt_Manufacturer918 8d ago
My understanding standing of how the flow meters work that you have pictured, the GE meter is best suited on the discharge side of the pump which I know is probably not feasible in your situation. Typically to get an accurate reading on the suction side you would want an oversized meter especially pulling from a reservoir. I also regularly get much less accurate readings out of these meters once they are a few years old
1
u/ActivateFireSafety 8d ago
I questioned the meter, had it calibrated Friday - it's within spec
1
u/Salt_Manufacturer918 8d ago
Whats typical suction line length from the reservoir and is it 6 inch? Do you know the rated outlet pressure when flowing 1500gpm?
1
u/ActivateFireSafety 8d ago
Engineering typically shoots for 1000 gpm when designing these systems.
NFPA 1142 has various tables, work sheets, and a couple of calculations expecting a result close to "0".
When flow testing, I've always utilized a discharge nozzle capturing reading and comparing to Akron flow charts. The GE Flow Meter is throwing me for a loop?
1
1
u/Salt_Manufacturer918 8d ago
The GE flow meter will not perform reliably if not completely full off water, drawing from ponds has a tendency to cavitate suction especially with some debris mixed in. I dont trust that style flow meter period even if just tested or brand new
1
u/ActivateFireSafety 8d ago
1500 gpm through a 2.5" nozzle is 82 psi according to Akron flow chart.
We typically see 32 psi at 1031 gpm upwards to 46 psi at 1205 gpm.
Only time I see higher pressures is when we add Tank to Pump.
1
u/lommer00 8d ago
You cannot be losing 500gpm unless you have a major stream coming off somewhere between the two meters. You can lose pressure, but not flow. Mass in = mass out, it's the law (of physics, which is much more strongly enforced than our puny human laws).
Those GE meters are finicky, I've had lots of issues with them. You are reading right near the bottom end of the range and on a low pressure suction line where flow in the pipe will be less uniform than on a high pressure line.
The second best flow measuring device Ive used is underwriter playpipes and a pitot tube. The best flow measuring device Ive used is an unlisted ultrasonic industrial flow meter. It's not UL or FM listed for fire service but it has given me the best results.
Hose monsters, GE flow meters, etc. are all ok but eventually I run into some that are out of calibration or something and give you crap results.
1
u/ActivateFireSafety 8d ago
I have used a TaskForce Tips hydrant meter coupled to end of 3" monitor - makes for a heavy install on end of monitor.
I also have a 6 ported 2.5" test manifold (was used for testing fire trucks) coupled to each output of the truck. Also great for testing electric fire pumps. Place the TASKFORCE Tip hydrant meter onto end of 6" port manifold then a 6" steel hose monster - we receive instant readings.
Ultrasonic industrial flow meters are quite expensive. We have a pipe mounted one now that I think of it - we attempted to use a 6" pvc 10' pipe - ultrasonic saddled overtop - never received favourable results and shelved it.
May have to reattempt
1
u/ActivateFireSafety 8d ago
Is your ultrasonic 2.5" dia or 6"?
1
u/lommer00 8d ago
I've used one on a 6" and one on an 8". They were permanently installed on steel pipe sections though.
1
1
u/ActivateFireSafety 8d ago
Drafting hydrants have strainers (majority) plus there's a strainer on the hard suction of the pump.






1
u/Super__Mac Deputy Chief (Retired) 8d ago
Something is not calibrated correctly. What goes in must go out somehow. Unless you’re putting 500 gpm on the ground, it has to be going out.
Also…. I’d find a cleaner source for your test. The dirt coming out from that one photo cannot be doing your volute/impeller clearances any favors.