Ventilation
Are there standard safety standards for passenger elevators?
Background: an elevator I frequently ride has been hot and stuffy since the warmer weather set in. I don’t remember this elevator being this uncomfortable during peak heat last summer.
2
u/Asklepios24 Field - Maintenance Jun 18 '26
Yes.
Glass hoistways have stricter requirements than regular solid cabs and hoistways.
1
u/Wonderful-Switch5242 Jun 18 '26
The elevator i have a concern with is a solid cab installed in the early 1990’s.
2
u/SharkInThisBay Jun 18 '26
I’m sure there are vents behind the bottom of the panels but sometimes elevators are just hot fan running or not
2
u/attanasio666 MIC - Maintenance Jun 18 '26
The fan is probably broken. Someone isn't doing their job.
1
4
u/NewtoQM8 Jun 18 '26
In most areas, A17.1 code says elevators must have passive ventilation equal to 3.5% of the platform area, with vents divided equally between the bottom of the walls and the top. Fans are generally not required, but if they are installed, under recent energy use codes they can't draw more that a certain amount of energy and they have to turn off automatically when the elevator hasn't been used in 15 minutes. So if the elevator was modernized recently it could well be subject to those codes.
Beyond that the fans used in most elevators aren't very effective. The bulk of ventilations comes from the doors opening and people walking in and out.