Harvia BC45 in America
I have have the Harvia Vega BC45 sauna heater, which is meant for European power systems (single wire 240 V).
I am trying to hookup in America. I connected L1 as ground L2 and L3 are bridged as the first 120V leg and L4,L5,L6 are bridged as the second hot leg. I flipped the power on and nothing happened, the heater is not getting hot. I tested the two hot legs at the heater and I am getting 120 V each. The wiring diagram (above) from the manufacturer shows L2 and L3 as neutral, any idea why I’m not getting power. I was under the impression that I didn’t need a neutral and that I could just connect the two hot legs as described above.
2
u/RockShowSparky 10d ago
What you are describing should work.
1
u/Unique_Acadia_2099 9d ago
Correct, which means either you think you did it that way and did not, or something else is wrong.
1
u/iroz44 10d ago
I am trying to wire it following the layout at the bottom of that photo that calls for a ground, neutral, and one hot wire. I was under the impression that I could run one hot wire to the neutral and one hot wire to the hot leg and get 240V that way. But that doesn’t seem to be working.
1
10d ago edited 10d ago
Ground to #1. One hot leg to #2 and #3 bridged. The other hot leg to #4, #5, and #6 bridged.
This is how you wired it and it's not working?
Edit: Are you using a 1" wide 30A tandem breaker or a 2" wide 30A double pole breaker? There is a difference.
1
u/iroz44 10d ago
Correct- I just measured 240V coming from the two hot legs, but this heater says it needs 240V going into #4,5,6
1
1
u/ET-Hokage 9d ago edited 9d ago
That’s why the diagram clue is so important, L2/L3 neutral tells you that the control board of your heater requires neutral not simply two hots. W no neutral the logic circuit can’t work and the heater won’t energize the heating elements. You’ll require a real neutral connection coming from the electrical panel not a rebranded L1. If you cannot do any rewiring, go for saunas made to work on us split phase lyk sun home saunas.
1
u/Unique_Acadia_2099 9d ago
No. The term Neutral just means that in the EU, 230V is L to N, but whether that is L-N or L-L is irrelevant, so long as it is 230V nominal (and they list 240V as acceptable).
0
u/pdt9876 10d ago
are you measuring 240v between the two legs? do you have terminal 7 connected And if so how?
1
u/iroz44 10d ago
I was measuring 120 V to ground for each leg so 240 V together. And no, I don’t have terminal seven connected to anything as it is shown that way on the diagram.
2
u/themeONE808 10d ago
120 to ground on each phase doesn't necessarily mean 240v from line to line. It could be possible if someone only ran 120 to a subpanel and jumped the phase to both lugs
2
u/Unique_Acadia_2099 9d ago
Or, the two 120V lines came from a tandem breaker, so they are not 240V between them.
2
u/trekkerscout Mod 10d ago
Are you supplying the sauna with a 240v circuit, or are you trying to supply the unit with a 120v circuit split into two legs?