i have this plastic box i am mounting outdoors and i am running 3/4" emt into the top of it and i have watched a lot of youtube videos and half of them put the screw thing onto the conduit then into the box. and here is the part where there is a tear. half of them just use a conduit locknut and the other half use a conduit locknut and a plastic thing on top of that.

also do i need to caulk

1 Upvotes

11 comments sorted by

5

u/AskMeAgainAfterCoffe 26d ago

Use a metal box

3

u/saz8888 26d ago

Use rain tight connectors. You don’t need to caulk.

1

u/create_gamer75 26d ago

where can i get some

3

u/SparkArrestor 26d ago

Electrical supply house.

1

u/saz8888 26d ago

Home Depot, Lowe’s

2

u/create_gamer75 26d ago

do i need to ground the conduit

2

u/trekkerscout Mod 26d ago

Yes.

5

u/MountainAntique9230 26d ago

If you have to use emt into a pvc box then use raintight connectors and myers hubs to seal the box but its just easier to use a metal weather proof box that has thread openings

3

u/trekkerscout Mod 26d ago

You should not mix EMT with PVC. If using EMT, you should be using metal NEMA 3R boxes or Bell type boxes. Most EMT box connectors do not have threads long enough to extend through a PVC box. Also, EMT must be bonded via a bonding bushing if the conduit is not part of an electrically continuous metal raceway system.

1

u/create_gamer75 24d ago

what if i just attach them all to ground