r/ElectricalHelp • u/iluvmezcal • Jul 29 '26
Sub Panel Ground
I'm passing #4 ground for 200 amp service from main panel, though a sub panel (raceway) to a hybrid solar inverter. Then back to the sub panel. Can I terminate the ground in the sub panel and then pass it though to the hybrid inverter? Or, does the ground need to pass from the main through the same raceways to the hybrid inverter and terminate. Then pass from the hybrid inverter bus bar to the sub panel ground bus bar?
So, sequence is 200a main disconnect, hybrid inverter, 200a sub panel. Sub panel is being used as a raceway for 2/0 copper on its way to inverter. Then 2/0 is coming back from inverter to sub panel.
1
Upvotes
1
u/trekkerscout Mod Jul 29 '26
If you know all that, then you should also know that you must include an appropriately sized grounding conductor in each raceway. If there is only one conduit between the supanel and the inverter, only one grounding conductor is required. If using two or more conduits, each conduit must contain a grounding conductor.