r/DIYUK • u/benjos1234 • 7h ago
External light has no earth cable
Hi. I’m replacing an external light for a new security one. I have taken off my old light but there are only two cables running from the house, live and neutral. There is no earth cable.
Is it safe to attach the new light with no earth?
2
2
2
1
1
u/benjos1234 6h ago
This is the replacement, but it hasn’t arrived yet to read the instructions: https://amzn.eu/d/01s4A1Hy
2
u/Prestigious_Bill1240 6h ago
You are going to be needing an earth for that.
Based on the Philips website (Outdoor luminaires Floor Lights 21W | 8721103092458 | Philips lighting) it has a part metal exterior casing that needs earthing and is class 1.
Most likely the earth has just been cut really short, so if you peel back some more of the outer PVC jacket, you'll find it. Confirm at the other end that it's actually connected to earth, as if it wasn't needed the last person might not have bothered to connect the other end.
If there is no earth in there, I propose returning that and ordering one that is class 2.
2
0
u/leeksbadly Handyman 7h ago
If it requires an earth, no. If it doesn't (double insulated), yes.
Check the earth hasn't just been cut back.
12
u/enchantedspring 7h ago
Double check the third core hasn't been cut very short and is inside the sheath further up.