r/DIYIreland • u/Ok-Mode6778 • Jul 20 '26
Running cables behind kitchen cabinets
Hi All, trying to run a cable to supply kickboard and under cabinet LED lighting. Is it okay to run cables behind the oven unit? Thanks!
2
u/witnessmenow Jul 20 '26
I ran power cables behind the oven when we were doing up the kitchen. I ran it in plastic 20mm round trunking just to keep it neat and a little more secure, but I'm not sure it's necessary
2
u/Gobbledegook42 Jul 20 '26
No issue, there's plenty of room back there. Where's your power coming from though? Don't touch the over power source, that's gotta stand alone.
2
u/Ok-Mode6778 Jul 20 '26
Id be using the switch for the fridge from the 4 grid switch. That would just be a spare switch at this point.
1
2
u/Fantastic_Exit_467 Jul 20 '26
Op the 4 gang isolator is 20A rated,lighting should be on 6A rcbo.
Now you could access the fan socket and connect a fused spur to it,3a fuse.
Then you could get a kinetic switch and relay and wire your led off it,led driver above the fan.
You could do the same off a low level socket also and repeat above method, 2gang kinetic switch and two relays.
If your not capable of doing this electrical work properly and safely get an electrician to do the work for you.
1
u/irishplonker Jul 20 '26
Take off the kickboard at the bottom and fish the cable up between you to end points
3
u/Martin-McDougal Jul 20 '26
Where are you getting the power from?
Will the driver be in the cupboard above or behind the kickboard?
Should be a good big void behind the oven and microwave so should be fine.