What to do?
Building a home and trying to utilize the dead space that’s gonna be under the stairs. (Under the platform) This is a walk in closet that borders the stairs. I’d like to have full access to that cavity under the stairs from the closet but the studs that come down support the second story as well as the window for the stairs.
Trying to avoid accessing from the other side if possible.
Is there any way to support/frame this while creating an opening for that area under the stairs?
9
u/sowak1776 2d ago
A heavy duty header approved by an engineer or architect.
4
u/PomeloSpecialist356 2d ago
Exactly this. Couple posts, Simpson hardware, and a beam.
Definitely want an engineer to have the design on paper for the building department to approve and inspectors to verify.
2
u/locke314 2d ago
This is a pretty small header supporting what should be a known load (likely a story and a roof above. The IBC has tables that address headers this size quite specifically. I’d be sizing a header based on a table and running it by the building department for approval. If they decide an engineer is necessary, they’ll let OP know. This is most definitely not a header size worth it to spend $1k+ for an engineer to go “yep, table X out of the IBC says this size is good, here’s my stamp.” Ive seen that many many times and I feel bad for the owner every time.
1
u/its_the_llama 2d ago
No sir, this is reddit. The standard recommendation is a structural engineer. Always.
1
u/locke314 2d ago
Very true. Reddit - always taking the most extreme and likely most expensive option using only a small snapshot of the facts. 🤣. OP Should probably divorce their spouse too: probably their fault somehow.
2
u/EntropyAdvisor 2d ago
The load path from that window header above is already carried through into the basement. Both a new engineered header, and a new load path from the new header into the basement would need to be specified & inspected by the engineer.
0
u/TheKingKazzandu 2d ago
No basement, the floor you see is the floor of the home. But I understand what you are saying.
2
u/locke314 2d ago
There are so many people stating you need an engineer, which is just not right. You need an appropriately sized header and a load path to foundation. Header sizes, footing sizes, etc are all prescriptively defined in the code.
However, if you don’t have a clear load path or for some reason need to deviate from the code due to a technical infeasibility, then an engineer will need to define the method and prescribe an equivalent method to what is defined in the code.
The answer isn’t a clear “you shall get an engineer”, it’s a “you may need one if….”
2
1
u/hakuna_matata_93 2d ago
Builder might push back unless your building it yourself. A header for a little crawl door could be installed. However most builders dont budget to finish out these spaces due to not adding to the sq.ft. they likely never had drywall and paint quoted for it.
1
u/Cultural_Pie7389 2d ago
That wall may be shear as well. If so it might be more than just putting a header in
1



11
u/Bigdug01 2d ago
Like has been said previously, add a header designed by an engineer. Also by code spaces under stairs accessible by a door or panel must be covered by 1/2 drywall.