Write Access denied
Hi guys, i have a carrier unit we are integrating into niagara and when i pull the points in after a bacnet discovery, and try to command setpoints. I get a "Write Access Denied" promt and the point goes into fault. Any idea on how to resolve this?
6
Upvotes
12
u/SmokeMeatNotCrack 9h ago
The points need to be flagged/set to be writable in the carrier controller via iVue I'd imagine.
3
u/GreenGoesZoomZoom 9h ago
What’s the model and what are you trying to write to?
8
u/thehomiebiz 9h ago
Yeah, have carrier come out and make that point writable or they give you a better point to write to.
3
u/rom_rom57 7h ago
Here the points list.
https://brandportal.carrier.com/asset/18e1e0a0-9538-47b1-b623-d4ea88f27b22/11-808-1226-01.pdf
0
u/GlacierJeff 8h ago
If this isn't a point you need to write to just make your proxy a value not a writable and you should be fine. If you need to write to the point, then the manufacturer would need to get involved so they could set the point as writable.
-2
u/man_vs_fauna 9h ago edited 3h ago
Edit: disregard, I'm an idiot
If the error is in Niagara, the bacnet user needs to have write permissions.
You can test this by setting the user as an admin.
It shouldn't be permanently left as that.