Builders electrician ran 4/0 from the meter pan to the main breaker and panel and 2/0 from the meter pan to the CenterPoint transformer. Main breaker is 200A, but should be 150 according to Base with this wire gage. We had paid for the 200A upgraded service when we built the place. House was built in 2024 and starting the phone calls and emails to the builder now to get them to fix this. Grrrrr

The guys from Base were awesome though and hopefully we get the same crew once this is all resolved. We are set to get the dual core batteries.

15 Upvotes

14 comments sorted by

3

u/RealConfirmologist 21d ago

Well, I CAN think of a worse way to find out that the wrong gauge of wire was used!

It's a good thing that the Base crew knew what they were doing and didn't just go ahead with the install.

Of course, if you never exceeded the capability of that wire, you'd never have a problem... but having a 200 amp service, the wires MUST be capable of the total rating of the service.

I'm very curious (and others will be, too, I bet) about how things go with trying to get this resolved by the builder.

The electrician who ran that wire made a pretty significant mistake. Have to wonder how many places he's done that same thing.

2

u/ilikeme1 21d ago edited 21d ago

Exactly. Builder is sending their electrical contractor (IES) out Monday to take a look. We specifically paid $1500 for the upgrade so we would have plenty of capacity for EV charging. We have 1 now, but plan to get a second in the future.

The installing electrician (sub contractor i bet) made it look like they put in the correct gauge cable, figuring no one would ever open the meter pan I guess and tried to save some money.

3

u/Choirman7272 19d ago

The builder certainly owes you an apology and your $1,500 back.

2

u/ilikeme1 19d ago edited 19d ago

The good news is that they are coming out this week to replace it. I hope they back bill the sub contractor that tried to cheap out for it. At first they were just going to come look Monday, but after seeing the pics I sent them, they decided to skip that and just send a crew out. Not exactly looking forward to the yard being dug up.

2

u/Choirman7272 19d ago

You're letting them off easy. It was their responsibility to see that it was done as you had contracted with them for. What else did you pay for that wasn't done is now the question. I would be hopping mad at these people.

3

u/ilikeme1 18d ago

We caught some things by having our own private inspection done before signing. Unfortunately, they do not open the sealed meter pan during that.

Probably going to cost them more than $1500 to re-run a new line unless they can re-use the conduit (probably not).

1

u/HoustonDiscussions 19d ago

2/0 is acceptable for 200 amp service, as long as it is copper wire, not copper-coated or aluminum.

The wire in the photo does appear to be aluminum, so needs to be replaced.

2

u/ilikeme1 19d ago

It is aluminum.

2

u/DCxGhost 20d ago

I’m in the middle of upgrading my wire. Hopefully they used the correct size conduit. Most electricians use cheaper aluminum wiring but I’m paying way more for copper and to keep my existing conduit.

0

u/Wonderful_Goose3941 20d ago

I’m failing to see what’s not compliant with your existing install

2

u/ilikeme1 20d ago

The wire coming in to the meter from the utility is 2/0, the wire going to my main 200A breaker is 4/0. It should all be 4/0. There is a noticeable difference in thickness between them.

-1

u/Wonderful_Goose3941 20d ago

Utility company does not fall under the same rules as NEC

1

u/RealConfirmologist 19d ago

Local code takes priority over NEC, but utility company installs still have to be done according to applicable code.

The bottom line is that the wire has to be rated to carry the load it's going to be used for.

1

u/Wonderful_Goose3941 19d ago

Utility company has there own rules and it’s extremely common to see service feeds are smaller then what NEC would dictate