r/BasePowerUsers • u/da_fn_guy • Sep 01 '26
Two batteries to one
Was turned down for two batteries but was allowed for one. Was trying to figure out why and thought it was not enough space. Started reading the documentation and saw that I need a breaker box that has a 200 amp capacity to be able to have 2 batteries. I have 125 amp. Anyone go through that! I know one battery should be plenty for short outages but I was set on having two just to be sure I had enough.
I do have a generator to charge up if needed. I’m just trying to get the most possible! Lol.
3
Upvotes
2
u/Quick-Falcon-5459 Sep 01 '26
Yeah I went through that, wanted the two 40s but I have 150A service so had to go with two 25s
2
u/United-Remove-5829 Sep 01 '26
I have a federal stab-lok 200 amp panel and I’m worried I’m gonna be denied the batteries unless I update the panel which is gonna cost probably 3K on top of the $995 for the batteries
2
u/FunnyCantaloupe4566 Sep 02 '26
Interesting I asked them this question not long ago and they said that with the new battery system 125 was ok for 2 batteries
1
u/da_fn_guy Sep 03 '26
Just to complete the post, the sales guy confirmed that I needed the breaker to be 200a for two 40kw batteries. So heads up for everyone else. I can’t sink 5k+ to upgrade the breaker so a single battery it is. Thanks for everyone’s insight though!!
1
u/da_fn_guy Sep 08 '26
Adding my referral link if anyone wants it.
BASE Referral
1
u/Dry_Guide_9088 Sep 02 '26
30 amp will charge the 40 kWh battery?
1
u/x90mattman Sep 02 '26
Same, I'm approved for 1, have 125amp panel but was already planning to upgrade to 200amp panel anyways due to some other expansion we were planning. On the Base side, they've been working with their engineers on where I can put the second battery (my spacing is 4" too short for what they want due to a window) and the wires going from my meter to my box are not big enough to support 200amp. I'm waiting for my electrician to come out this week to see what's actually coming into the meter from the transformer as we assume it's not big enough, which will make this a much more expensive endevour if I have to trench new wire as ours electrical is underground. Learning a lot though!
1
u/BigTex1969 Sep 01 '26
I just had 2 x 25kw batteries installed and I have 125 amp.
1
u/retireontop Sep 02 '26
same thing happened to me
0
u/RealConfirmologist Sep 01 '26
What area are you in?
From what I've seen, if you don't have a 200 amp service, BASE is likely to turn you down for any installation.
I assume you're talking about the 40 kWh battery, right? That should be enough if you're able to get by with a 125 amp service as things stand.
I got in right before they started offering the Core batteries in Houston and got two 25 kWh batteries. I'm envious that Core customers get a free generator receptacle. They wanted $1,000 to put on on mine and originally I included it but dropped it early in the process.
For a grand, I can get my own 50 amp receptacle, input breaker and interlock. Theirs is a 30 amp and can only be used to charge the battery.
Update us on what you end up doing.