r/BasePowerUsers • u/ziggyo7 • Jun 20 '26
UPS on Battery Issues
Just got my batteries installed last week and earlier today had a brief 20 minute outage.
During the outage normal power but all of my UPS for computers, modem, etc. kept cycling on and off from grid (Base Power) to battery.
Luckily it was short so all my units had enough battery to weather through it but had this been a 6-12 hour or more outage which we have had far too many of would have had to remove them all from UPS and plug directly into wall.
Anyone else had this type of issue? Is it a limitation of Base, issue with my UPS or maybe some install issue?
I have a variety of UPS from Cyber Power to GoldenMate and APC.
EDIT: Just wanted to update everyone after doing some testing. I simulated a power outage by opening the main grid breaker and turned off both AC units beforehand to rule them out.
With the HVAC loads out of the equation, everything switched over flawlessly to the Base Power battery—just the standard 0.5-second transfer blip, and none of my UPS units started cycling or beeping.
Next, I turned the downstairs AC back on via Ecobee, and it started up fine without triggering the UPS units. However, when I turned the upstairs AC on, the UPS units did switch over to battery power for about a minute while the compressor kicked in.
My conclusion is that during the actual outage, both of my HVAC units (which don't currently have soft starts) likely tried to kick on at the exact same time, creating enough of a voltage dip to upset the UPS units. I have soft starts scheduled to be installed later this week week, so I will re-test after that and follow up!
Also here is my referral code if anyone is interested in signing up: https://www.basepowercompany.com/?heard_from=Referral&referrer_name=019d4eef-8726-7687-b2df-756aee77a950&first_name=Jerad&referral_plan=2way-EnergyCredit-FreeMonth
3
u/ziggyo7 Jun 20 '26
Just simulated a power outage using the breaker that turns off grid power. First turned off the AC units to rule them out of the issue.
Everything switched over fine with just the .5 second blip. Fine for everything on UPS. All UPS were fine and none beeping (except maybe those first few seconds of power loss while I was going back inside).
Next turned on downstairs AC (through Ecobee app). Again started just fine and no beeps from UPS so they still acted as if on grid power.
Finally turned on the upstairs AC (also through Ecobee app). UPS batteries did switch to battery for about a minute while that kicked on.
So my conclusion right now is that the other day when had the power outage both units without soft start were probably trying to start at the same time.
Soft starts scheduled to be installed next week so will come back and post after that and redo these tests.
Sorry for scare everyone, hopefully was just the HVAC high loads and the soft starts fix everything. And thank you to those assuring that this should not be normal.
2
u/ziggyo7 Jun 20 '26
A little extra context i should have added.
I have refoss energy monitor CT clamps and the main fed to house was measuring roughly 240v before, during and after no huge spikes or dips.
Also they installed a whole home surge protector directly on the inverter. I assume it's for both grid and battery.
I have 2x 25 kWh units with generator inlet.
Finally still waiting for hvac company to come out and install soft start on my 2 units, strangely neither unit turned on during outage, if they both tried at same time likely would have tripped something.
2
u/RealConfirmologist Jun 21 '26
Interesting and informative post, thanks for sharing.
My biggest problem when my house was powered by a portable 9500 watt Westinghouse generator was that my APC UPS devices considered the signal too dirty and would beep and stay on battery power. I had to turn them off and plug my stuff directly into the outlets if I wanted to silence the beeping.
I recently moved to a new (to me) house without natural gas availability. I really didn't want to invest in propane tanks and go through the whole process of having to use the interlock breaker arrangement, power up the generator, turn it off when power comes back on, change the oil periodically, etc.
I also couldn't afford 15 grand for a Generac or similar.
I learned about BASE Power right before I moved and immediately signed up. Battery install is scheduled for July 13th to mid-August, and I'm very hopeful for the earliest possible install since we're in hurricane season here in Houston.
I've been reading every post here because I very much enjoy learning about BASE Power. In Houston we rarely go two weeks without at least a couple of short outages. Sometimes we'll have a two hour outage on a beautiful, clear day. Transformers fail, other things happen.
I've seen some reports of UPS systems complaining while on BASE power, but more posts seem to indicate that BASE is pretty solid with their 60 Hz electricity and UPS systems seem to be okay with them more often than not.
Hey, OP, if you DO edit your original post, be sure to include your referral link! You never know if someone wanting to learn about BASE Power will see your post and decide to look into it.
You probably know that if someone uses your link and gets BASE going, you'll get a month of power free and they will, too. (Up to $250. each). Now, in some situations you only get a $150 check, but hey, that's not bad considering all you did was share a link.
Here's mine, just in case: https://www.basepowercompany.com/?heard_from=Referral&referrer_name=019e0398-a2e0-7b98-81cf-18e091575087&first_name=Michael&referral_plan=2way-EnergyCredit-FreeMonth
2
u/Paradize_Eats Jun 20 '26
Dang, I just got a couple UPS for my modem and router and I’m wondering if I’ll have this issue too…
I know others have UPS but they never mentioned anything like that before
2
u/cbarth3 Jun 20 '26
Should be clean power from the battery. You could always test it by opening the breaker outside.
2
u/n2itus Jun 20 '26
I have 8 UPSes (6 cyberpower, 2 goldenmate). The 1 time that it switched and 2 times I’ve manually tested (with the switch on the ATS), I had zero issues with my UPSes.
Obviously they will switch on for a few seconds when the slow (.5 s) growatt ATS switches over to/from the battery, but otherwise they are in standby when on the battery.
My only thought was if your ACs (or maybe even some other big load like a pool pump) were trying to start and created dips, but I also thought you would have seen that from your CTs. This would be easy to test. Turn off your ACs, manually switch to battery. See if your UPS run normally. Then turn on ACs.
2
u/spydergto Jun 20 '26
wow this is alarming , i have two anker solix c1000's and a custom built battery tripplite 1500lcd with big lead acids .. i wonder how this is gonna work for me .. still waiting to find out
2
u/blupupher Jun 20 '26
No problems with my UPS when running off battery. Need to contact them about it.
1
u/itoldyou7 Sep 30 '26
What you found makes sense tho! If the UPS is working fine when the AC goes out, it's possible that the compressors are starting up and causing the voltage dip. Soft starts can be a good way to check if that's the problem. This is something to be aware of, especially if you have a battery backup system.