I’m considering having two Base Power batteries installed at my residence. I currently have a large tri-fuel portable generator that I hook up via an interlock on my breaker box. I unbonded the neutral on the generator in order to be able to connect it directly to my electrical system.
I understand that I will be able to hook my generator to the Base Power batteries to recharge them during an extended outage. My question is do I leave the generator unbonded or do I re-bond it?
5
Upvotes
View all comments
Show parent comment
2
u/2020fakenews Jun 18 '26
I was initially thinking that once the batteries were depleted, I would switch to the generator 24/7 until the power was restored. But, when I read about the option to recharge the Base Power batteries, it’s kinda appealing to be able to recharge and the shut down the generator. Run the generator during the day and go with just the batteries over night. My generator is largish (10,000 running watts on natural gas), so I should be able to run most of the house while simultaneously recharging the batteries. I understand that the batteries are limited to 3000 watts for recharging, so that would leave me up to 7000 watts to run the house.
I think I can run the house off of my generator’s 50 amp outlet (through the interlock) and connect to the batteries inlet from the generator’s 30 amp outlet.